Earthquake demand
The first step is to determine the earthquake demand on all of the components that make up the engineering systems within the building. This is the procedure to determine earthquake demand:
- Classify the building importance level and component categories.
- Determine the earthquake load demand (static forces).
Find out about:
- Component categories
- Calculating earthquake load demand
- Determining relative displacement
- Other design considerations
Component categories
NZS 4219:2009 Table 2 sets out general objectives and performance requirements for each component in an engineering system. This requires the designer to classify all components on the basis of the consequences of their expected performance under earthquake actions.
Criteria |
Component category |
Limit state |
Component represents a hazard to life outside the building |
P1 |
ULS |
Component represents a hazard to a crowd of greater than 100 people within the building |
P2 |
ULS |
Component represents a hazard to individual life within the building |
P3 |
ULS |
Component necessary for the continuing function of the evacuation and life safety systems within the building |
P4 |
ULS |
Component of a system required for operational continuity of the building |
P5 |
SLS2 |
Component for which the consequential damage caused by its failure is disproportionately great |
P6 |
SLS1 |
All other components |
P7 |
SLS1 |
(From NZS 4219:2009, provided by Standards New Zealand under licence 001149)
Note that category P5 only applies to importance level 4 buildings as this is a requirement of NZS 1170.5:2004. Design loads derived for components in lower importance level buildings may be increased unnecessarily if category P5 is applied instead of P6 or P7 to other components in importance level 1, 2 and 3 buildings.
Calculating earthquake load demand
The earthquake load demand (F) on a component for each design criterion should be calculated by multiplying the lateral force coefficient (C) by the operating weight of the component (W) in the equation:
F = C x W
The lateral force coefficient can be found using the component’s height (CH), the building’s earthquake zone factor (Z), the component performance factor (Cp) and the component risk factor (RC) in the equation:
C = 2.7 x CH x Z x Cp x RC
where CH is 3.0 for components that are above the ground floor or 1.0 for components that are on or below the ground floor. C need not be greater than 3.6.
Earthquake zones
The earthquake zone factor (Z) represents the relative level of seismicity for the building’s location in New Zealand. It can be determined from NZS 4219:2009 or NZS 1170.5:2004 or derived from the following map. These must all be modified in accordance with Amendment 10 of the Building Code citation of NZS 1170.5:2004. This states that, for buildings in the Canterbury Earthquake Region with a building structure period less than 1.5 seconds, the zone factor should not be less than 0.3.

Relative seismicity for the design of seismic restraints for engineering systems. (From NZS 4219:2009 Figure 2, provided by Standards New Zealand under licence 001149)
Performance factor
NZS 4219:2009 Table 4 provides for a performance factor (Cp), which can be used to determine the load on each part of the restraint system.
Component |
Importance level |
Component category |
Performance factor (Cp) |
Anchors, fixings and fasteners |
1, 2, 3, 4 |
All |
0.85 |
Braces and supports |
1, 2, 3, 4 |
P1, P2, P3, P4 (ULS) |
Lower of 0.85 or from the table below |
Braces and supports |
1, 2, 3 |
P6, P7 (SLS1) |
0.85 |
Braces and supports |
4 |
P5 (SLS2) |
0.85 |
(From NZS 4219:2009, provided by Standards New Zealand under licence 001149)
NZS 4219:2009 Appendix C shows normative performance factors for specific components and their specific type of installation.
Component |
Type |
Restraint |
Performance factor (Cp) |
Horizontal or vertical piping |
Steel, flanged joints Steel, welded or grooved joints |
|
0.45 |
Steel, screwed joints |
|
0.65 |
|
Copper, brazed joints |
|
0.55 |
|
Polypropylene |
|
0.25 |
|
Horizontal or vertical rigid ducting (including in-line components) |
|
Suspended and braced to the structure |
0.45 |
Rigid metal exhaust flue |
|
Braced to the structure |
0.45 |
Cantilevered from its base |
0.55 |
||
Cable tray |
|
Suspended and braced to the structure |
0.45 |
Tank (non-pressure) |
Floor mounted |
Ductile base fixing |
0.55 |
Limited ductile base fixing |
0.85 |
||
Braced to the structure |
0.55 |
||
Directly attached to a timber or steel wall (such as hot water cylinder) |
0.55 |
||
Directly attached to concrete or masonry wall |
0.85 |
||
On a stand |
Two-way moment-resisting stand |
0.45 |
|
Braced to the structure |
0.55 |
||
Pressure tank (for example, LPG tank) |
|
Floor-mounted cradle |
0.85 |
Compact component (boiler, pump, solid-fuel burner) |
Floor mounted |
Ductile base fixing |
0.55 |
Limited ductile base fixing |
0.85 |
||
Vibration isolation |
0.75 |
||
Braced to the structure |
0.55 |
||
Suspended |
Suspended and braced to the structure |
0.55 |
|
Non-compact component (such as chiller or cooling tower) |
|
Floor mounted |
0.45 |
Metal cabinet (such as electrical, communication, rack-mounted computer equipment) |
|
Floor mounted |
0.45 |
Braced to the structure |
0.55 |
||
Light fitting (excluding lights mounted on suspended ceilings) |
|
Directly fixed to the structure |
0.85 |
Suspended and braced to the structure |
0.55 |
(From NZS 4219:2009, provided by Standards New Zealand under licence 001149)
Risk factor
The component risk factor (RC) can be determined from NZS 4219:2009 Table 5 using a known importance level and component category. Note that, following the 2010–11 earthquakes, the component risk factor for buildings in the Canterbury Earthquake Region should not be less than 0.33.
Component category |
Risk factor (RC) |
||
Importance level |
|||
1 and 2 |
3 |
4 |
|
P1, P2, P4 |
1.00 |
1.30 |
1.80 |
P3 |
0.90 |
1.20 |
1.60 |
P5 |
NA |
NA |
1.00 |
P6 |
0.50 |
0.50 |
0.50 |
P7 |
0.25 |
0.25 |
0.25 |
(From NZS 4219:2009, provided by Standards New Zealand under licence 001149)
Determining relative displacement
Components connected to the building structure at more than one level must be designed to sustain the relative seismic displacement (D) between the levels for the appropriate design criterion.
The displacement can be determined from the building’s calculated design displacement, where known. If the displacement is not known, it may be calculated using the component risk factor (RC), the height between fixing points (HZ) and the following equation:
D = 0.025 x RC x HZ
Note that, when using this equation, RC should be no greater than 1.0.
The non-specific design pathway allows relative displacement to be accommodated using flexible joints. The joints must be able to accommodate the relative displacements between fixing points. Where a component is attached to the structure using rigid joints that are not designed to allow for the relative displacement, the component must follow the specific design pathway.
Other design considerations
In building design, the role of engineering systems in protecting life and property and providing safe egress from the building should be considered along with seismic resistance of services and their components. The basic concepts of a building layout should be examined against the likely effect of earthquakes on the particular building.
The effect of heavy equipment on the structure and other building components should be considered. Heavy equipment breaking loose is a potential source of injury and building damage. Locating heavy plant at a high level within the building not only adds to the earthquake loading, it may require pipes and electric power to run the full height of the building.
The seismic resilience of connections to public utility services should be assessed. The design should aim to reduce the probability of damage and provide for connection to temporary alternative services when required. Vehicle access, mains pipe connections, the position of shut-off valves, meters, risers and main reticulation are all important.